On the AHU version 2.0 onward, the Re-heating coil, when set to Compensation, will modulate to achieve the minimum Supply Air temperature limit setpoint defined in Gfc07.

The strategy of this implementation is found on the 1TOOL Sheet:  Heat_Cool_Coil_Humidifier

In the Version 1.x of the FLSTDmAHUE software, the Re-heating coil operation when humidifying will "compensate" the action of the De-hum (if set in compensation or Comp+int) and try and achieve the Temperature setpoint on the Supply Air (as suppose to the regulation probe) set on the screen Gfc28.

This will define the % Opening of the Re-heating coil.

This should point you in the right direction on the settings we where looking at just before you left the office.

  • Flag

Your Answer

Please try to give a substantial answer. If you wanted to comment on the question or answer, just use the commenting tool. Please remember that you can always revise your answers - no need to answer the same question twice. Also, please don't forget to vote - it really helps to select the best questions and answers!