In the Carel Standard AHUE software, you have the possibility to control the inverter via MODBUS directly from the PCO controller if it is fitted with a PCO100FD10 Modbus Master serial card. You will need to wire the inverter to the PCO100FD10 MODBUS Field card of the controller as per instruction on the DOC file downloadable HERE. You will also have to configure the inverter parameters as indicated in the same DOC file (the motor parameters will have to be configured accordingly).

You will have to enable in the AHU program in the manufacturer section (Mask Ha03) the fans type  set to "Inverters" and then configure the MODBUS Master on mask Ha25.

ATTENTION: Please make sure that the inverters are powered up at all times. If the power fails to the inverters the Carel controller will give an offline alarm on it's display.

You may find the documentation of the inverters by clicking on the links below:

Further information on the modbus communication between the Inverters and Carel controller are also found in the User Manual of the AHUE software downloadable here.

  • Flag

Your Answer

Please try to give a substantial answer. If you wanted to comment on the question or answer, just use the commenting tool. Please remember that you can always revise your answers - no need to answer the same question twice. Also, please don't forget to vote - it really helps to select the best questions and answers!

Ask a Question

Want to be updated when new questions are asked?

About This Forum

For all your support requirements regarding CAREL, Belimo and all things HVAC

 About

Question tools

2 follower(s)

Stats

Asked: 11/19/15, 10:00 AM
Seen: 675 times
Last updated: 7/11/17, 1:12 AM